Question: When derating feeder conductors, does the number you finally derate to for the conductors have to be more than the breaker size of the circuit you are installing, or more than the calculated load?
For example, I have a #3 THHN 100 amp feed, 3 ph. with double neutral installed in a 2" conduit for bus duct (3 hots, 2 neutrals, 1 grd). I am wanting to pull another set of #3's in this conduit, making a total of 10 #3's and the #8 ground. The conduit is of sufficient size, and the neutrals are not current carrying conductors since they only carry the unbalanced load (and not a lot of non-linear load).
So that leaves me with 4-6 Current Carrying Conductors, which I derate 80%. 310.16 shows 110 amps for #3 in the 90C column, multiplied by 80% is 88 amps.
There is an example in the 2005 NEC Handbook showing branch circuit calc. for a 20 amp circuit, and it shows only needing the conductor to be above 16 amps, or 80% of the 20 amp breaker allowed loading after doing all the derating/temp. adjustments. It uses 210.19 A 1 to allow this.
Is this the same for the feeder in my example? Do I just need to have a conductor above 80 amps (or 80 % of the 100 amp breaker)?
Thanks for any advise!!!
For example, I have a #3 THHN 100 amp feed, 3 ph. with double neutral installed in a 2" conduit for bus duct (3 hots, 2 neutrals, 1 grd). I am wanting to pull another set of #3's in this conduit, making a total of 10 #3's and the #8 ground. The conduit is of sufficient size, and the neutrals are not current carrying conductors since they only carry the unbalanced load (and not a lot of non-linear load).
So that leaves me with 4-6 Current Carrying Conductors, which I derate 80%. 310.16 shows 110 amps for #3 in the 90C column, multiplied by 80% is 88 amps.
There is an example in the 2005 NEC Handbook showing branch circuit calc. for a 20 amp circuit, and it shows only needing the conductor to be above 16 amps, or 80% of the 20 amp breaker allowed loading after doing all the derating/temp. adjustments. It uses 210.19 A 1 to allow this.
Is this the same for the feeder in my example? Do I just need to have a conductor above 80 amps (or 80 % of the 100 amp breaker)?
Thanks for any advise!!!