Derating for # of CCC

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If you run a 6 ckt EMT homerun(all 1p-20a for receptacles) from panel and each circuit is required to have separate neutral that would be 12 CCC. 2 questions.
1. Which column would you use from 310.16 75 or 90? I know it's based on terminal ratings but not sure about receptacle terminal ratings. Know they breaker would be 90 degree.
2. Since there would be 13 CCC you would have to reduce ampacity by 50% per 310.15?

Sent from my SM-N960U using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Assuming you are using 90C conductors you start at the 90 C column and start the derating. The final ampacity must not be higher than the 75C column.

This is assuming the panel has 75C or 90C terminals
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For #12 THHN it would be 30 amps * 50% = 15 amp circuits, for #10 THHN it would be 40 amps* 50% = 20 amp circuits.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So you're using the 90-degree column for ampacity. Why?

Sent from my SM-N960U using Tapatalk


Most conductors are rated 90C so you start from there based on the section David mentioned above

Conductors
with temperature ratings higher than specified for terminations
shall be permitted to be used for ampacity adjustment,
correction, or both.
 

victor.cherkashi

Senior Member
Location
NYC, NY
Recently I put two feeders in one conduit for two outdoor CU, but now I am not sure if I did it correctly.
(2) CU - 3-phase, 31MCA, 50MOP
Each CU fed by 50A circuit breaker.
#8 THWN-2 have to be derated from 55A to 44A (80% - 6 CCC in one conduit)
Question: Can I use 50A circuit breaker for each feeder or the c.b. must be below 44A?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Recently I put two feeders in one conduit for two outdoor CU, but now I am not sure if I did it correctly.
(2) CU - 3-phase, 31MCA, 50MOP
Each CU fed by 50A circuit breaker.
#8 THWN-2 have to be derated from 55A to 44A (80% - 6 CCC in one conduit)
Question: Can I use 50A circuit breaker for each feeder or the c.b. must be below 44A?

After the derating the conductors need to be a minimum of 31 amps (forget the OCPD size). As David stated in this application you could have used #10 THWN-2 with an adjusted ampacity of 32 amps (40*80%=32 amps) and the 50 amp OCPD.
 

kwired

Electron manager
Location
NE Nebraska
So you're using the 90-degree column for ampacity. Why?

Sent from my SM-N960U using Tapatalk
You have two things you need to comply with, termination temp rating and insulation temp rating.

For your 20 amp circuits you must have at least 12 AWG conductors for the termination temp rating. But you have no terminations in the raceway so all that matters there is insulation temp rating and the reason you begin adjustments/corrections from 90C ampacity.

But at same time after making adjustments your conductor must still be at least as large as what is required in 75C column (or even 60 C column) for the sake of the termination.
 