If you run a 6 ckt EMT homerun(all 1p-20a for receptacles) from panel and each circuit is required to have separate neutral that would be 12 CCC. 2 questions.
1. Which column would you use from 310.16 75 or 90? I know it's based on terminal ratings but not sure about receptacle terminal ratings. Know they breaker would be 90 degree.
2. Since there would be 13 CCC you would have to reduce ampacity by 50% per 310.15?
Sent from my SM-N960U using Tapatalk
1. Which column would you use from 310.16 75 or 90? I know it's based on terminal ratings but not sure about receptacle terminal ratings. Know they breaker would be 90 degree.
2. Since there would be 13 CCC you would have to reduce ampacity by 50% per 310.15?