Hello,
Building a house with PV. The Main Service Panel (MSP) and service coming to the house is 400 Amps. The MSP has two 200 Amp main breakers, one that protects the CBs in the MSP and the other that services a 200 Amp Sub-Panel (SP) in the middle of the house. The busbar in the MSP is totally independent of the branch that feeds the SP. The MSP busbar is rated at 200 Amps. A majority of house circuits are feed into the SP as a cost savings measure (wire is expensive these days).
The PV is 12 Kw and has 3 strings each with a 20 Amp CB into the MSP, or 60 Amps total. The other circuits in the MSP sum is 120 Amps so the total value of the CBs in the MSP is 180 Amps.
Here is my question - Do we need to de-rate the 200 Amp CB that services the MSP since the max load in theory could only be 180 Amps? The Solar Company is asking for a 175 Amp CB in that position but I think they are just trying to sell me a CB. I don't get it?
Thanks in advance, BillyBob
Building a house with PV. The Main Service Panel (MSP) and service coming to the house is 400 Amps. The MSP has two 200 Amp main breakers, one that protects the CBs in the MSP and the other that services a 200 Amp Sub-Panel (SP) in the middle of the house. The busbar in the MSP is totally independent of the branch that feeds the SP. The MSP busbar is rated at 200 Amps. A majority of house circuits are feed into the SP as a cost savings measure (wire is expensive these days).
The PV is 12 Kw and has 3 strings each with a 20 Amp CB into the MSP, or 60 Amps total. The other circuits in the MSP sum is 120 Amps so the total value of the CBs in the MSP is 180 Amps.
Here is my question - Do we need to de-rate the 200 Amp CB that services the MSP since the max load in theory could only be 180 Amps? The Solar Company is asking for a 175 Amp CB in that position but I think they are just trying to sell me a CB. I don't get it?
Thanks in advance, BillyBob