I see that Table 31.15(B)(2)(a) indicate the adj factor
however I have been told that an exception will allow more than 3 ccc in a conduit
my example
I have a single phase loadcenter (6) 20 amp circuits
(4) circuits to (4) 20a duplex receptacles
(1) circuit to interior lights (4) 4' 2 lamp 40 watt fluorescent
(1) circuit to exterior lights (4) 70 watt HPS flood lights
a hot, neut, and gnd for all circuits #12 AWG THHN in a 1 inch conduit over 24 inches
from what I know I have in this conduit 12 ccc so I should now derate to 50%
according to the table
the building is manufactured to customer specification we are an OEM
I have been told that I could reduce the size of the breakers or run separate conduit
I wanted to know if there is such an exception to this table that will allow the above ccc to be in one (1) inch conduit
or if there is an exception due to the fact we are an OEM manufacture
I am getting so many mixed comments and would like to know if there is such an exception
One other question I asked this before and wanted to get further advice to gain more knowledge of this and other sections of the code any good teaching books that anyone can offer would be great, I plan to sign up at a local collage for code training soon
Thanks
however I have been told that an exception will allow more than 3 ccc in a conduit
my example
I have a single phase loadcenter (6) 20 amp circuits
(4) circuits to (4) 20a duplex receptacles
(1) circuit to interior lights (4) 4' 2 lamp 40 watt fluorescent
(1) circuit to exterior lights (4) 70 watt HPS flood lights
a hot, neut, and gnd for all circuits #12 AWG THHN in a 1 inch conduit over 24 inches
from what I know I have in this conduit 12 ccc so I should now derate to 50%
according to the table
the building is manufactured to customer specification we are an OEM
I have been told that I could reduce the size of the breakers or run separate conduit
I wanted to know if there is such an exception to this table that will allow the above ccc to be in one (1) inch conduit
or if there is an exception due to the fact we are an OEM manufacture
I am getting so many mixed comments and would like to know if there is such an exception
One other question I asked this before and wanted to get further advice to gain more knowledge of this and other sections of the code any good teaching books that anyone can offer would be great, I plan to sign up at a local collage for code training soon
Thanks