I have been reading and reading and reading the Forum on this topic and I am now totally confused, perhaps I should just describe my application and see what exception if any may apply, or if I am on the right track, I have several questions and will separate them
The buildings / shelters manufactured all are built and shipped, all are OEM specific, so some may be mobile and some may become permanent after shipment. Some application are classified and some general purpose
I have this debate when routing the conduit throughout interior and exterior,
First of all we very rarely every have the final destination, so for a rule of thumb, should I use a standard temperature range
Q1) Temperature adjustment
Now the part I need the most help, derating
Example:
From my panel board or load center I have for this occurrence a single phase panel, I need help on sharing the neutral, to reduce the number of ccc from what I have been reading in a single phase application I can use the same neutral for several circuits, and more in a 3 phase application, most of the application require (1) HOT, (1) NEUT, & (1) GND per circuit,
I would like to reduce the number of wire fill, share the neutrals and reduce the number of grounds conductors and submit code to support this
Q2) Neutral & Ground
Were in the code can I study this
Now derating the conductors,
Example:
I have a 30 ckt panel and I have 20 ckt all too various components: receptacles, interior lights, exterior lights, exit signs, emergency lights, etc... wire size is typical #12 AWG THHN, and most of the circuits are on 20a circuit breakers I know now to reduce the breakers closer to the load required {i.e. exit sign on a 10a rather than a 20a} and allow for multiple ccc in one conduit based on table 310.15
From what I have been told the simple method is to run the circuits in individual conduits, this makes for an overwhelming amount of conduits however after reading I would like to know were in the code it will allow for anything outside this
Example:
I have (1) 1? EMT and 21 conductors (7) HOT, (7) NEUT, & (7) GND from what I have read this will be 14 ccc and the ampacity is now at 50% the #12 AWG conductors are now only rated for 10 amps so the breakers need to be 10 amp breakers,
During my reading I found that I can rate the wire by the load as well, now my confusion grows
Q3} Derating / Conduit fill what articles can I study this
Thank you all, I know that I need help in this area, and this is the place to find answers
Also if anyone can give me guidance to learning books or suggestion, I recently purchased the ?illustrated guide to the national electrical code? based on the 2005 code by Charles Miller
Any other reference books or sites in addition to the code book (I plan to get my own soon) would be great!!
Thanks again
The buildings / shelters manufactured all are built and shipped, all are OEM specific, so some may be mobile and some may become permanent after shipment. Some application are classified and some general purpose
I have this debate when routing the conduit throughout interior and exterior,
First of all we very rarely every have the final destination, so for a rule of thumb, should I use a standard temperature range
Q1) Temperature adjustment
Now the part I need the most help, derating
Example:
From my panel board or load center I have for this occurrence a single phase panel, I need help on sharing the neutral, to reduce the number of ccc from what I have been reading in a single phase application I can use the same neutral for several circuits, and more in a 3 phase application, most of the application require (1) HOT, (1) NEUT, & (1) GND per circuit,
I would like to reduce the number of wire fill, share the neutrals and reduce the number of grounds conductors and submit code to support this
Q2) Neutral & Ground
Were in the code can I study this
Now derating the conductors,
Example:
I have a 30 ckt panel and I have 20 ckt all too various components: receptacles, interior lights, exterior lights, exit signs, emergency lights, etc... wire size is typical #12 AWG THHN, and most of the circuits are on 20a circuit breakers I know now to reduce the breakers closer to the load required {i.e. exit sign on a 10a rather than a 20a} and allow for multiple ccc in one conduit based on table 310.15
From what I have been told the simple method is to run the circuits in individual conduits, this makes for an overwhelming amount of conduits however after reading I would like to know were in the code it will allow for anything outside this
Example:
I have (1) 1? EMT and 21 conductors (7) HOT, (7) NEUT, & (7) GND from what I have read this will be 14 ccc and the ampacity is now at 50% the #12 AWG conductors are now only rated for 10 amps so the breakers need to be 10 amp breakers,
During my reading I found that I can rate the wire by the load as well, now my confusion grows
Q3} Derating / Conduit fill what articles can I study this
Thank you all, I know that I need help in this area, and this is the place to find answers
Also if anyone can give me guidance to learning books or suggestion, I recently purchased the ?illustrated guide to the national electrical code? based on the 2005 code by Charles Miller
Any other reference books or sites in addition to the code book (I plan to get my own soon) would be great!!
Thanks again