I once did a mathematical analysis (just for the fun of it :grinI would think that in actuality there is hardly ever a case where there is a completely balanced load where a neutral would be carrying no current whatsoever.
Believe him. Even with the neutral connected, current will flow away from the panel on one phase conductor, through the one set of lights, then through the other set of lights back into the panel on the other phase conductor. When we say the neutral carries the unbalanced current, it also means that with a balanced load the neutral carries no current. So if you disconnect the neutral, it will not alter the current flow in any way.He stated that he accidently disconnected the neutral at the panel for these (2) circuits and all of the Lamps remained lit. I didn't know whether to believe him or not. . . .
It doesn't matter. It is impossible for the neutral to carry any current unless that current is reduced in (i.e., subtracted from) one or more of the line conductors. There can never be more than three conductors' worth of current.I would think that in actuality there is hardly ever a case where there is a completely balanced load where a neutral would be carrying no current whatsoever.
I believe what he really had was (30) lamps wired in series at 240v when he disconnected the neutral.
If you understand why a neutral isn't a CCC, you'd believe him.I didnt know wether to believe him or not,but never had the chance to try this for myself.
Actually, he had either 15 pairs of series-wired lights in parallel, or two 15-light paralleled strings in series. I tend to believe it was the latter, with a single neutral.I believe what he really had was (30) lamps wired in series at 240v when he disconnected the neutral.
Which is why the neutral is a CCC when derived from such supplies.If the supply system were208Y/120 the lights would stay lit but they would all become dim due to the fact that the VD across each light would be 104 volts.
No. There are 15 lights in parallel bewteen each line and the neutral, receiving 120v. When the neutral is lifted, the two sets of 15 lights are in series bewteen the two lines, receiving 240v. With the two groups in series, they split the voltage between them, and each sees 120v.When he disconnected the neutral in the panel, did he not send 240 volts across each lampholder less what voltage was lost across each filament?
O.k. someone help me get clear. I have a multiwire branch circuit sharing a neutral. Black, red, blue, white. From a 3 phase 120/208 4 wire wye. Do I have to count this neutral as current carrying? From what I understand, only if its a 3 wire mwbc, using 2 phases. What about this 4 wire branch circuit using all 3 phases, is there any difference?