dino629 said:NEC 310.15(4) (a)... I'm sure the answer is simple here, but is a neutral counted when you de-rate conductors, if not when does this paragraph apply???
dino629 said:When is the neutral considered to carry the "unbalanced load" of conductors?:-?
Correct, unless we're talking a high poercentage of high-3rd-order-harmonic-content loads.dino629 said:Just so I understand... If we packed a pipe with (12) #10awg all with 3 hots to a neutral, (not a 3 phase load, but A,B,C phases respectively to separate loads) then We are not counting the neutral as a current carrying conductor and would not have to derate accordingly? Thanks
Larry,Correct, unless we're talking a high poercentage of high-3rd-order-harmonic-content loads.
goldstar said:Larry,
Can you explain this a bit more ? I was eaves-dropping on a conversation that came up at my contractor's association meeting the other night where one of the contractors claimed that he no longer uses 12/3 MC when wiring circuits where electronic ballast fixtures are installed. Supposedly there is a large harmonic load on the neutral. Normally if you have a 15 amp load on one phase and a 10 amp load on another the neutral would carry the difference of 5 amps. From what I overheard in this case the neutral would be carrying 25 amps because of the electronic ballasts. Did I hear this correctly and if so can you explain ?
Thanks,
Phil
I'll try. Normally, the neutral carries only the difference current among the hot wires sharing it. Because the voltage peaks occur at different times, the total neutral current is only the imbalances; they subtract.goldstar said:Larry, Can you explain this a bit more?