- New Jersey
- Journeyman Electrician (retired)
Rob, To me Art 240 addresses overcurrent protection and Art 210 addresses the circuit. To me, 210.19 still requires the conductor to have an ampacity adequate for the load. ONCE you have selected that conductor, then you go to Art 240 and select the OCP device. Art 240 allows us to use that 20 amp breaker on any load (in this situation) up to 17.5 amps.
I have a problem with the assumption that the receptacle is the load. If 240.4(B) didn't want to allow single receptacle circuits to go up to the next standard size then why does that section use the word multi-outlet as part of the requirement? If it truly was concerned about something that may happen in the future then it should prohibit all receptacles from the next standard size rule. Clearly (to me at least