SiddMartin
Senior Member
- Location
- PA
I need to better understand derating of CCC in a conduit.
I am using #12 THHN cu, and in a conduit longer then 24", to derate, can I use the 90 deg. column? I believe I can and thus I figure this:
#12 is rated at 30Amps. (310.16)
If I have (7-9) #12 CCC's then 30 * 70% = 21 Amps . Am I okay to still protect the #12's w/ a 20A breaker? I think I am.
now if I have (10) #12 CCC then 30 * 50% = 15A, I would have to either protect the #12's w/ 15A breaker or upsize to #10 THHN. Am I correct in thinking this>? I believe so b/c (10) #10 CCC is 40A * 50 = 20A,
am I missing something to the equation or am I correct?
I am only questioning solution to derating the # of CCC, not anything else
Thank you in advance
I am using #12 THHN cu, and in a conduit longer then 24", to derate, can I use the 90 deg. column? I believe I can and thus I figure this:
#12 is rated at 30Amps. (310.16)
If I have (7-9) #12 CCC's then 30 * 70% = 21 Amps . Am I okay to still protect the #12's w/ a 20A breaker? I think I am.
now if I have (10) #12 CCC then 30 * 50% = 15A, I would have to either protect the #12's w/ 15A breaker or upsize to #10 THHN. Am I correct in thinking this>? I believe so b/c (10) #10 CCC is 40A * 50 = 20A,
am I missing something to the equation or am I correct?
I am only questioning solution to derating the # of CCC, not anything else
Thank you in advance