derating of conduit and wire run above roofs

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Which makes no sense to me. Why change the ampacity of a wire for a difference of 5 degrees of ambient temperature but not for a 30 degree rise because it is laying on the roof in direct sunlight?

Simple, lack of evidence that it was needed.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Simple, lack of evidence that it was needed.

If I remember correctly this was one of those sounds like a good idea, theoretical code changes based on the idea that the hot roof would impact the conductors when in fact there was not a lot of real world evidence to support that claim. Sorry to say that the NEC seems to be moving in that direction for several code cycles.
 