markebenson
Senior Member
- Location
- fl
Say i have (wye) (2) 20a circuits in (1) 20ft section emt. Adustment factor d310.15(b)(3)(a) does not apply because I have just 3 ccc's. black, red, white
Now scenario 2 I decided to split each 20a circuit into 4 switched circuits with with same 20a supply each set of 4.
Now I have 4 black, 4 red, 1 white in the emt (plus green of course).They will each terminate to edisons.
Do i now have 9 ccs in this conduit? Or do I use the 3 ccc number because the switch legs are powered by just the 2 20a circuits.
Thanks
MB
Now scenario 2 I decided to split each 20a circuit into 4 switched circuits with with same 20a supply each set of 4.
Now I have 4 black, 4 red, 1 white in the emt (plus green of course).They will each terminate to edisons.
Do i now have 9 ccs in this conduit? Or do I use the 3 ccc number because the switch legs are powered by just the 2 20a circuits.
Thanks
MB