7-150a Log #CP700 NEC-P07
(334-80)
Final Action: Accept
Submitter: Code-Making Panel 7
Recommendation:
Add a new paragraph to 334.80 to read as follows:
"334.80 Where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing which is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a)."
Substantiation:
Code-Making Panel 6 Rejected Proposal 6-31 to add the proposed text to 310.15(B)(2)(a) and provided the following Panel statement: "The Panel agrees with the intent of the Proposal, however, this material is more appropriately addressed in 334.80 since the Proposal only applies to one type of cable, and Code-Making Panel 6 covers all wiring methods. Therefore, Code-Making Panel 6 has forwarded this Proposal to Code-Making Panel 7 for action."
The substantiation provided by the submitter, Travis Lindsey, of Proposal 6-31 was:
"Recent experimentation shows the possibility of dangerous conditions when loaded circuits are brought into close proximity to each other inside a fire- or draft-stop, where the ability to dissipate heat is extremely limited. Cable temperatures well in excess of their 90?C rating were encountered, with no overcurrent protection present for these conditions. Results indicate that immediate adjustments should be made to the NEC to apply at least to the specific case represented by the experiment. Such a proposal is being made, with a supplemental report offered as technical support."
Panel Meeting Action: Accept