In the general sense, no. But many line-to-line equipment fall under the more specific Articles which may place such limitations on these circuits.One of the reasons for the separate breakers for the welder/plasma (#1) & mill/lathe (#3) was because my understanding is that 230VAC loads each require their own means of disconnect. Is that correct?
In many cases, yes. But then we get into the more specific Articles and it could be no. Even in the general sense, 110.58 requires a transformer (most welders are, in a sense, enhanced transformers) or motor (which I'm certain the mill/lathe has at least oneIf so, then is a plug and receptacle considered a "disconnect"?
The fused disconnect I mentioned is because the only way the 30A circuit can be considered a feeder is if you tap off it*, which will require the tap conductor to be smaller than the feeder (if the same size it would not be a tap). Tap rules require termination of the tap conductor's load end to a single ocpd (the fused disconnect)(Note: These are not large industrial machines, so I think a fused-disconnect is overkill. Unless that is a requirement for them to be on the same branch.)
* As others have stated, another option is to feed a subpanel.