In all seriousness, can I?Throw away that chart and use the proper values from the NEC.
In all seriousness, can I?Throw away that chart and use the proper values from the NEC.
Did you happen to see the note that I posted from that chart in post #15? The values in this chart are no help for what you're asking. When derating a 90° C, #12 conductor you use the ampacity of the 30 amps in the NEC Article 310, T310.16.In all seriousness, can I?
I'd leave it and sleep well tonight.Would you leave the installation I mentioned earlier, or rip it out?
IThe cable gets sleeved into the EMT and then enters into the box. I believe that a minimum of 1/4" of jacket is required in the box. Not being allowed to remove the jacket is stupid but unless the conductors are marked you're not supposed to remove it.