I see it as a very dangerous response as it says that the hot wires are USUALLY on different phases or legs. That suggest they can be on the same phase of leg which will overload the neutral.What do you think of ChatGBT response?
View attachment 2579431
Not sure how you have opposite phases when it's only 1Ø.What do you think of ChatGBT response?
View attachment 2579431
We've discussed this plenty, on this site. The voltage waveforms on the black and red wires, are mathematically equivalent in the ideal case, to two waveforms that are 180 degrees apart. Yes, I'm aware of the technicality, they are not separate phases, due to how they are produced, but I can understand why someone might call them "phases", despite the technicality.Not sure how you have opposite phases when it's only 1Ø.
That was my point, the AI that was quoted in this thread is incorrect. IMO for a single phase 120/240 volt system the word leg is more suitable and should be used in lieu of phase.The voltage waveforms on the black and red wires, are mathematically equivalent in the ideal case, to two waveforms that are 180 degrees apart. Yes, I'm aware of the technicality, they are not separate phases, due to how they are produced