I see it as a very dangerous response as it says that the hot wires are USUALLY on different phases or legs. That suggest they can be on the same phase of leg which will overload the neutral.What do you think of ChatGBT response?
View attachment 2579431
Not sure how you have opposite phases when it's only 1Ø.What do you think of ChatGBT response?
View attachment 2579431
We've discussed this plenty, on this site. The voltage waveforms on the black and red wires, are mathematically equivalent in the ideal case, to two waveforms that are 180 degrees apart. Yes, I'm aware of the technicality, they are not separate phases, due to how they are produced, but I can understand why someone might call them "phases", despite the technicality.Not sure how you have opposite phases when it's only 1Ø.
That was my point, the AI that was quoted in this thread is incorrect. IMO for a single phase 120/240 volt system the word leg is more suitable and should be used in lieu of phase.The voltage waveforms on the black and red wires, are mathematically equivalent in the ideal case, to two waveforms that are 180 degrees apart. Yes, I'm aware of the technicality, they are not separate phases, due to how they are produced
I wonder if that was Lake Panasoffkee Elementary School? I have a feeling we may have talked to each other on the phone. I just checked my plans and the Engineer is from Clearwater! When I saw this post I immediately though of the same thing. If it is you, then for others, we were in an existing school with a dedicated HVAC panel, so it also had no neutral. We had to jump through hoops and get a neutral in from 300 feet away in one building. Luckily the conduit was sized large enough. If it is you, then I will just say, it was a pleasure. I am sure most of us here know how adversarial the relationship between and Engineer and an electrician can be. This was an excellent exchange.I have recently done a project where the condensing unit of a 5 ton mini-split system (480V, 3 phase) that required a neutral because the ECM motor for the fan was 277V. It was Daikin unit.
It was and you must have been talking to my Engineer. Glad it all worked out. First time we have ever had a mechanical piece of equipment like that require a neutral.I wonder if that was Lake Panasoffkee Elementary School? I have a feeling we may have talked to each other on the phone. I just checked my plans and the Engineer is from Clearwater! When I saw this post I immediately though of the same thing. If it is you, then for others, we were in an existing school with a dedicated HVAC panel, so it also had no neutral. We had to jump through hoops and get a neutral in from 300 feet away in one building. Luckily the conduit was sized large enough. If it is you, then I will just say, it was a pleasure. I am sure most of us here know how adversarial the relationship between and Engineer and an electrician can be. This was an excellent exchange.