Not to start a thread with in a thread but couldn't you protect it with an 80A 240.4(B)?
You can as long as the calculated load is not greater than 75 amps.Not to start a thread with in a thread but couldn't you protect it with an 80A 240.4(B)?
You can as long as the calculated load is not greater than 75 amps.
Thanks just did not know if there was something that trump Art 240 on this...funny I am on this job I took over and the have most of the materials there two sub panels going in two 100A breakers, well now that I read this (did not know this but now will never forget) instead of them eating the cut 2AL SER cable I will just have them return the breakers and get two 80 amp. Did the load calcs and they are bother under 50amp but never know what is going to be added. If this sounds like a bad way to go I am sure I will hear it. Just hate to have this customer eat the wire but hate more for the cable to melt.
side note I wonder how many times a feeder in this situation gets under sized ...
Thanks to the OP (and those that answered)
OK; Just got pointed to 31O-15(B)(6), and what I missed is that this table also refers to the main power feeder between the main disconnect and the panelboard that provides branch circuits to a dwelling unit. 2/0 for 150 amp will fine as usuall. If a 2nd sub panel leaving the main distribution panel is installed, I'de have to refer to table 310-16 @60c, and have to make choice to either install a derated SER cable, or install smaller sized conductors from 310-15(B)(6)in a conduit. I think the inspector was just stresing out still many electricians were still using #2 SER leaving main panel going to a 100 amp sub panel, and if failed, just stick a 90amp breaker in place, but @60c, would only be good for 75amp(70A brkr).
Howard richman
My other question is: Does 334.80 for NM which also applies to SE cable supercede table 310.15(B)(6)??
IMO, no.... In Gus' opinion Yes...:grin:My other question is: Does 334.80 for NM which also applies to SE cable supercede table 310.15(B)(6)??
See post #20.
Unfortunately Nec 2011 does nothing to clear the air however it allows se cable to exclude 334.80 except where installed in thermal insulation.
This is big, at least as I think I understand it now, as it means that most applications of SER as a subpanel feeder (among other applications of SE cable that isn't actually service entrance duty) will allow use of the 75C ampacity, rather than the 60C, as long as it's not run in thermal insulation. Unless I'm wrong on this.
I was actually searching for discussions on this change, and came across this thread, which only grazed the topic.