joeyww12000
Senior Member
- Location
- Chatsworth GA
Heres the deal, I have conductors of 18awg and 14awg to be pulled in a 1 1/4" pvc conduit. These conductors will be feeding door locks for jail cell doors. Problem is they should have been in at least 4 seperate conduits for this application but we have what we have, there not in the slab and its to late. Anyway the total of the conductors is 24 14awg and 32 18awg, totalling 56 conductors in this 1 1/4" PVC conduit. Besides being hell to pull, how do I figure derating on this? Does the load being served have any impact? There isnt a constant load, only when doors open and close.