Derating wire exception in 2008 NEC code

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
In NYC we are stuck with 2008 NEC with amendments.

In the updated code 310.15(B)(2)(a) exception it says "Adjustment factors shall not apply to conductors in raceways
having a length not exceeding 600 mm (24 in.)."


However in the 2008 NEC it does not say that. It only gives the exception for nipples and not raceways specifically: "Exception No. 3: Derating factors shall not apply to conductors in nipples having a length not exceeding 600 mm (24 in.)."

If I'm under the 2008 NEC, does this mean I still have to derate wires that are less than 24 inches in the raceway?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Wireways have a different set of rules. Derating doesn't apply until you have more than 30 CCC's at a cross section.
 