If you used the method I proposed, "648A actual x 1.25 = 810A rated and 810A rated / 0.58 = 1396 A total ampacity required. 1396/4 runs = 349 amps per ckt. The minimum size conductor is 500 kcm at 380 amps is adequate. " and compare it to this method "rated load = 810 amps. Using 90C rating 500 kcm 430 amps x .58 = 249.4 amps x 4 = 997.6 the results are the same as far as conductor size required. However if you use the 1000 amp breaker the 500 kcm is not correct. I think the 2nd calculation is the way it is usually done but would the 1st calculation be incorrect? Any comments?
I'll give it a go. The first calculation is incorrect, because the adjusted/corrected ampacity need only be adequate for the load to be served, which is 648A. 648A/0.58 = 1117. 3 sets of 400mcm 90C would be adequate for the load (380A*3*0.58= 661A.)
However, as you noted, a conductor with an ampacity of 661A is not properly protected by a 1000A OCPD (or an 800A OCPD for that matter.)