2 offices.
receptacles office 1 circuit 1
receptacles office 2 circuit 3
lighting for both circuit 5.
Single phase service all 20 amp circuits.
If I pull a neutral ro each circuit (to get away from having to use handle ties) looking at 6 #12's and 1 grnd
easily fits in 1/2" emt.
If I wire them as MWBC's and use handle ties 5 #12's and 1 grnd.
Next 2 offices #3 and #4 same way only circuit 2 and 4, but with same lighting circuit.
If I try to catch both offices with (1) 3/4" conduit (Which would hold 10 or 12 #12's easily) I've violated the derating seeing as how there would be at least 10 CCC's which would derate the thhn to 50% and drop me to 15 amp max on the circuits.
Seems Odd
JAP>