Howard Burger
Senior Member
- Location
 - N of Anchrage, AK
 
T310.13 tells me XHHW is rated at 75 degrees in wet locations.  We are planning on pulling 10 ccc underground for a bull rail, which would require 50% derating.   Since XHHW is 75 degree wire in wet locations, can I still use th 90 degree column of T301.16 to derate the #10 from 40 to 20 amps, or do I need to use the 75 degree value?  I see XHHW is shown under 'types' at the top of both the 75 and 90 degree columns.
	
		
			
		
		
	
				
			
				