Re: *****DERATING*****
To get 600 amps through one set of conductors, you need size 1500 MCM. 3? EMT will only hold one of these.
To get 600 amps through two parallel sets of conductors, each must be able to carry 300/0.8, or 375 amps. For this, you need size 400 MCM. 3? EMT will hold six of these. If you don?t need a neutral, it might be possible to sneak 6-400?s and a #1 EGC in to a 3? EMT, but you?d have to calculate it by % fill and by cross-sectional area of the conductors. The Annex C Tables don?t give you room to include the EGC.
To get 600 amps through three parallel sets of conductors, each must be able to carry 200/0.7, or 286 amps. For this, you need size 250 MCM. 3? EMT will hold nine of these. Once again, if you don?t need a neutral, it might be possible, as discussed above.
In either of the parallel cases, you're likely to have trouble actually executing the pull. So I?d agree with Bob ? it's not going to happen.