Re: *****DERATING*****
I do not think anyone forgot about 240.4(B), you forgot to tell us the actual load on the conductors.
240.4(B) will let you move up to the next OCPD.
BUT, the load on the conductors still has to be less then the conductors are rated for.
Example. If the ampacity of the conductors is 570 amps and the load is 550 amps you could use a 600 amp OCPD, but if the load is 580 amps you can not use the 570 amp conductors.
I do not think anyone forgot about 240.4(B), you forgot to tell us the actual load on the conductors.
240.4(B) will let you move up to the next OCPD.
BUT, the load on the conductors still has to be less then the conductors are rated for.
Example. If the ampacity of the conductors is 570 amps and the load is 550 amps you could use a 600 amp OCPD, but if the load is 580 amps you can not use the 570 amp conductors.