question, if i have 8 400kcmils and 1#1 ground going in 4"conduit. table 310.16.
75 degree cable at 400kcmil you have 310 time 2 = 670 time .7 = (70%)=469amps i am told by a electrician that the code sayes when you derate you can use the 90 degree column which gives you 380 times 2= 760 = 532amps is this correct and where does it say that.
thank you for your help.