hey i have a silly question. is there any time when you wouldnt count a neutral as current carrying conductor in a derate situation. example. i have 3 20A,125, 3wire single phase twistlocks (each with own neutral) and one 20A 120/208, 5 wire 3phase twistlock all in a single 3/4 emt home run. so does that makes 9 or ten current carrying conductors, do i count the neutral in the 3phase 5wire 20A or do i disregard that conductor since its 3phase? had this question at work and just trying to clarify for own benefit.oh its all THHN awg.
 
Re: derating ?

Assuming linear loads, if you put all the 125 v twist locks on different phases (i.e. ABC) and used one neutral, it would not be current carrying and would not be counted.

The neutral for the 5 wire receptacle most likely would not need to be counted, once again, this is dependant on the load.

Roger

[ May 19, 2005, 08:41 PM: Message edited by: roger ]
 
Re: derating ?

As Roger said, if the 5 wire circuit were for a Linear Load than the netural would not count, so you would have 9 current carrying conductors.
 
Re: derating ?

they asked for the sep neutrals on the 125 twistlock. so i can disregard counting the neutral then on the 5wire then for my derateing. can u clarify when u say linear load.
 
Re: derating ?

The neutrals in the 2 wire circuits are counted, the neutral in the 5 wire isn't if the circuit is linear. This means that the 5 wire circuit does not contain a non-linear load which is caused by triplen harmonics. Harmonics become additive in the neutral due to a distortion in the sine wave, so the neutral will carry current up to 1.73 times the phase current. Therefore circuits with non-linear loads must have their neutral counted as a current carrying conductor.

[ May 19, 2005, 10:53 PM: Message edited by: infinity ]
 
Re: derating ?

how do i know if the 5wire is linear or not? can u give some examples where there are 5wire both linear and not. boy this forum rocks with info and help :D
 
Re: derating ?

It has nothing to do with a 5th wire. It has to do with where the major portion of the loads are non-linear when applying the derating factors required in 310.15 on a three phase 4 wire Y circuit.

310.15(B)(4)(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
Edit to ad that non-linear loads are electronic ballast, equipment with switching power supply's, or any load that switch's on and off at a higher frequency rate than the supply's 60hz.

[ May 20, 2005, 12:27 AM: Message edited by: hurk27 ]
 
Re: derating ?

these particular circuits are comming out of a 400Hz panel instead of the standard 60. that make any diff
 
Re: derating ?

Originally posted by cisco28:
these particular circuits are comming out of a 400Hz panel instead of the standard 60. that make any diff
Probably not, since most switching power supplies operate in the kHz range.

By "linear", we mean that the voltage and current are mostly in phase, because there is little reactance (capacitance and inductance collectively).

Examples of linear loads would be resistive loads like incandescent lighting and resitance heating. Computers are notoriously non-linear loads.
 
Re: derating ?

By Cisco28: these particular circuits are coming out of a 400Hz panel instead of the standard 60. that make any diff
Not on the derating issue but it will affect the rating of the breakers.
Check with the manufacture of the breakers to see how much you have to derate the breakers.
 
Re: derating ?

Wayne is right, you need to talk to a manufacturer and let them tell you what their equipment can do at 400hz, this is what I do on 400hz installations.

Skin effect at elevated hz's can change what we normaly see at 60hz.

For example

;)

Roger

[ May 20, 2005, 09:00 PM: Message edited by: roger ]
 