Years ago I had a service call in a copy center. After three years in thier new location, they started tripping breakers and couldn't figure out why. In the 'back copy room' were 15 copy machines.... the big ones they use when a customer comes in and says "I need 100,000 copies by tomorrow!". So they crank up all 15 machines and run them all night.
Someone had originally installed a 2" pipe from the panel to a 20x20 pull box in the ceiling above the copy room and wagon-wheeled 1/2" and 3/4 conduits from there. All 15 copy machines were run in that 2" run with AWG12s, as well as the lighting, GP circuits and other copy machines. 90% of the building load was in that 2".
Turns out, there were 15 full boats (45 circuits!) in that pipe, and the insulation was melting off some of them. I abandonded the original 2" and piped several smaller conduits in.
'Twas a nightmare doing it, and I wish I had a camera back then... you guys would have either laughed your heads off or chucked your supper.