I am rewoking circuits into an existing 120/208 panel to accomadate for a future generator.
The existing branch circuits are fed into the panel from a 2" pipe. I calculate that I need at least 42 current carrying conductors in the 2" pipe. I think these should be #10awg but my boss says that #12 awg is ok.I work in Massachusetts and Table 310.15(B)(2)(a) has been amended to allow 21-42 conductors to be derated to 60%. Any thoughts?
The existing branch circuits are fed into the panel from a 2" pipe. I calculate that I need at least 42 current carrying conductors in the 2" pipe. I think these should be #10awg but my boss says that #12 awg is ok.I work in Massachusetts and Table 310.15(B)(2)(a) has been amended to allow 21-42 conductors to be derated to 60%. Any thoughts?