don_resqcapt19 said:Bob,
Take a look at 250.30(A)(1) Exception #2.
Don
Yes I knew about that.
It is not relevant to the point I was trying to make.
don_resqcapt19 said:Bob,
Take a look at 250.30(A)(1) Exception #2.
Don
LarryFine said:I would consider the main bonding jumper to be entirely within the transformer enclosure. The conduit is merely the feeder's EGC. Now if, say, the GEC's are bonded at the source, but the neutral bonded at the panel, that would be using the conduit as a jumper.
Make sense?
infinity said:It's funny Bob, but my 2005 Handbook .....
iwire said:So what your saying is,
Bob stop being cheap get a 2005 NECH.![]()
![]()
Maybe not, but you specified PVC between the panel and the transformer and that can put the exception into play depending on the mounting methods and building structure.Yes I knew about that.
It is not relevant to the point I was trying to make.
I agree that the conduit cannot be used as a system bonding jumper, but I don't see how it would ever be anything other than an EGC. If you place the system bonding jumper in the transformer the raceway to the panel is the EGC for the panel and its circuits. If you place the system bonding jumper in the panel, the raceway is the EGC for the transformer.I hear you Don, but help me out here. Lets forget the PVC and say I used RMC. Can I use the RMC as the systems bonding jumper as Larry was pointing out? Obviously I do not think so.
don_resqcapt19 said:Bob,
I agree that the conduit cannot be used as a system bonding jumper, but I don't see how it would ever be anything other than an EGC. If you place the system bonding jumper in the transformer the raceway to the panel is the EGC for the panel and its circuits. If you place the system bonding jumper in the panel, the raceway is the EGC for the transformer.
Don
Pierre C Belarge said:Bob
250.30(A)(2)
You are correct that it is an equipment bonding conductor, but there is no code requirement that it be a wire. If it is a wire it is sized by 250.66.I agree it would be sized per 250.66.
That alone should signal that it is not an EGC.