Replacing a Main lug only sub panel in a garage.
#2awg aluminum is existing. Hoping the feeder is on a 90amp breaker as it’s already existing.
Customer wants a main breaker in garage for ease of adding stuff and working in panel.
I plan to just use a sub panel with a 100amp main as that is a standard size in the big box stores with the amount of spaces I need.
To keep from a fused or knife switch disconnect or other methods is anybody else seen #2awg aluminum feeding a 100amp subpanel if the feeders protected at 90amps.
I know the conductors are properly protected with the feeder breaker but just wondering if this is the norm for this scenario.