From a pure technical standpoint, I don't believe 225.30(D) even matters for this. As you say, headings matter, and 225.30 is "Number of Supplies". A 3-way switch-loop from additional building to the originating building and back is not a "supply". It would have to power a load at the originating building for it to be a "supply" there, which it does not, and it does not constitute a second "supply" when it returns to the additional building for that is where the "building supply" originated. :roll:
You should be a politician. :grin: