George I did read the last sentence and every word in both sectoins.
First 338 states that the cable is required to be supported as outlined in 334.30 which means that the cable is to be supported.
In 334.30 the key word in that last sentence is ?sections? meaning ?parts? of the cable being protected not the entire cable. These sections would be those that pass through masonary walls, floors or sections that are in danger of damage such as subject to traffic. Sections in no way means the entire cable.
Now with all that has been said about the SE cable being underground it is clear that UL does not list the cable for installations underground in direct burial no in a raceway. The listing found in the Wiring Manual that You posted is very clear that SE type cable is for aboveground installations ONLY as I will once again post so all can read.
SERVICE ENTRANCE CABLE (TYLZ)
GENERAL
This category covers service entrance cable designated Type SE and Type USE for use in accordance with Article 338 of ANSI/NFPA 70, ?National Electrical Code? (NEC).
Service entrance cable, rated 600 V, is Listed in sizes 14 AWG and larger for copper, and 12 AWG and larger for aluminum or copper-clad aluminum. Type SE cable contains Type RHW, RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors. Type USE cable contains conductors with insulation equivalent to RHW or XHHW. Type USE-2 contains insulation equivalent to RHW-2 or XHHW-2 and is rated 90?C wet or dry.
The cable is designated as follows:
Type SE ? Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
Types USE and USE-2 ? Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on
single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun.
Submersible Water Pump Cable ? Indicates a multiconductor cable in which 2, 3 or 4 single conductor Type USE or USE-2 cables are provided in a flat or twisted assembly. The cable is Listed in sizes 14 AWG to 4/0 AWG inclusive, copper, and 12 AWG to 4/0 AWG inclusive, aluminum or copper-clad aluminum. The cable is tag marked ?For use within the well casing for wiring deep well water pumps where the cable is not subject to repetitive handling caused by frequent servicing of the pump units.? The insulation may also be surface marked ?Pump Cable.?
The cable may be directly buried in the earth in conjunction with this use. For termination information, see Electrical Equipment for Use in Ordinary Locations (AALZ).
As you can see the SE/SE-R types of Service Entrance cables are listed for above ground installations.
USE is listed for both underground and direct burial and if it has the tag or mark it can be used in wells. The Pump Cable can also be a direct burial cable.
The one thing that I am sure of is SE and SE-R is
NOT ALLOWED to be installed underground in any fashion.
georgestolz said:
As your
recent feedback from the UL indicates, the term "underground" refers to the wiring method that is in direct contact with the soil surrounding it.
The aboveground listing of SE/SE-R takes all other issues out of play. It does not matter what type of conductor is in the cable when it is listed for aboveground.
georgestolz said:
Reconstruct this sentence in plainer english:
If you install enclosures or raceways underground, the cables and insulated conductors installed inside the enclosures or raceways shall be listed for use in wet locations.
Can we reconstruct this sentence
Type SE ? Indicates cable for aboveground installation.
to say something like this:
?Keep this cable aboveground at all times?
georgestolz said:
iwire said:
Mike, MDP we are not going to agree here.
It's not a big deal, if anybody other than us has been following along they can clearly see the points on either side and make their own decisions.
mpd said:
I agree with iwire, this is not going to get settled here, both sides have strong opinions and are not going to change...
Quitters.

:lol:
George most of the time when playing poker people will fold when they are not holding a winning hand. We can?t call them ?quitters? just because they are wrong.
Remember there is always you and me and we can take this to the big 1000 all by ourselves as long as we don't get locked out.