slick 50
- 6 super bowl ring city
Why do you need to run a seperate ground conductor in the pvc pipe? Doesn't the 12-3 uf have a grounding conductor in it? If you install a panel out in the shed, you will need a means of disconnect in it even though it is a subpanel because it is considered an out building. Install your ground rods and run a #6 bare between them and then to the panel.
A 20a 120/240v 12/3 UF underground feeder to a detached shed. If the source breaker is a 2-pole, we have a MWBC, and we attach lights to one line and receptacles to the other, we still need a 2p disco, right?
But, if we put in a 4- or 6-space ML panel, we need an electrode system, too. We'd need 2 rods, not smaller than #8 cu GEC, and it can't be bare wire. How far can each end be bare and still be covered?
The PVC runs from 24" below grade and ends at the floor, and will not run to the panel, so the UF and GEC will be visible. I want to run the GEC through the same 1" PVC sleeve. I may just use #6 anyway.
Any reason the rods and the GEC and jumper can't be buried in the same trench as the UF? Have I missed anything?
Danke,[/QUOTE]
Danke,[/QUOTE]