I have a residential customer who wants to have two 20 amp circuits run from his 200 Amp panel out to a shed that's located about 90' from his house. I suggested the installation of a subpanel, but my customer stated that he only wants two circuits.
Anyway, I believe the only way I could accomplish this is by adhering to Article 225.30. I would have to run a multiwire branch circuit (Considered a single circuit) that will originate from a 20amp double pole breaker in the 200 amp panel. Where the circuits enter the shed, I was planning to use a 20amp double pole toggle switch as a disconnecting means. Am I on the right track?
I really don't like the idea of sharing a neutral. Thoughts on the neutral as well?
Anyway, I believe the only way I could accomplish this is by adhering to Article 225.30. I would have to run a multiwire branch circuit (Considered a single circuit) that will originate from a 20amp double pole breaker in the 200 amp panel. Where the circuits enter the shed, I was planning to use a 20amp double pole toggle switch as a disconnecting means. Am I on the right track?