Customer has a 10×12 shed that was converted into an office. They want a plug circuit and a lighting circuit. Since the shed is detached, does it need to have a subpanel?
Not for a single circuit or a single MWBC, but a 1p or 2p disconnect switch is required.Customer has a 10×12 shed that was converted into an office. They want a plug circuit and a lighting circuit. Since the shed is detached, does it need to have a subpanel?