That panel can be mounted with main on top or bottom, there is no "upside down".Hard to tell from the picture. Panel mounted upside-down? Ok to have mini-breakers in those locations? No bonding bushing on the incoming 2" (250.92)?
I've got to be honest. The home was abandoned and they said that the panel had several violations in it. I've looked this whole thing over and I'm not seeing anything that sticks out at me. I thought maybe a wire guage or the fact that those conductors are not connected to a breaker but that wouldn't be a violation. I'm stumped also.
Who are "they"? & which code cycle are they expecting the panel to be compliant with? If "they" are a home inspection service that would explain alot
tYes, its a home inspection service. It's an abandoned house and I have no access to the report. They stated the issues with the panel needed to be addressed and I'm not seeing it. I'm beginning to doubt my own abilities. :blink:
seeing the CU & undersized neutral it appears the feed into the panel is a piping system -- that said/assumed is there a disconnect ahead of this panel on the structure & would this be considered a feeder? All indications otherwise points to this being the service lateral which appears compliant.
Different AHJ's have different allowances on how far service conductors are allowed to enter a building before they must hit the service disconnecting means. If that were a building on a slab and less then 5 feet before hitting the panel - it would be ok here.seeing the CU & undersized neutral it appears the feed into the panel is a piping system -- that said/assumed is there a disconnect ahead of this panel on the structure & would this be considered a feeder? All indications otherwise points to this being the service lateral which appears compliant.
Looks maybe like for an air conditioner/heat pump that is no longer there, may have been taken out because the unit was removed and this would prevent energizing the exposed conductors?The only thing I found related to the system is this ripped off disconnect in the back yard which obviosly needs to be redone and this was obvious though.
View attachment 17387View attachment 17388View attachment 17389
Only thing I see is the white conductors used as ungrounded conductors are not identified. I see the green screw so ok to have N and G together (some people like to keep them separate anyway, for appearance).
Yes, you are.Am I the only one who is seeing a bare #6/#4 ground wire on the bottom lug that doesnt go to squat? It just appears to die at the bottom of the panel.
Yes, you are.
There is usually a small hole in that area for the GEC. At least there is on the panels I use.