We are currently performing an Arc Flash Evaluation on two or our plants electrical systems for two plants we have on site. We first ran all of the Arc Flash calculations and PPE levels for each plant individually and establised a PPE level at each piece of equipment with each plant isolated and operating seperately as they do during normal operation.
There is a tie-breaker between the two plants that is only closed during an emergency situation where one of the plants looses its utility feed. With the tie breaker closed both plants can be operated at reduced capacity off of the one remaining utility source.
With this tie breaker closed this may present a scenario where the fault contribution from one plant to the other through the tie breaker changes the Arc Flash level at the busses in each plant calculated when each plant was isolated. This may also change the PPE at each bus.
How is a situation/scenario like this usually handled with Arc Flash PPE labels to account for this emergency situation? Are there certain assumptions that are made?
Do you treat the tie-breaker as an emergency situation and therfore only establish PPE values on equipment for condition where plant is isolated?
Do you try to come up with a best estimate on what loads will be running on each plant and try to calculate a sepearate Arc Flash and PPE value and then use the worst case of this vaule and the one calculated when plants were isolated for establishing PPE requirement?
Do you just issue a blanket statement/requirment saying that during an emergency situation where tie-breaker is closed you must dress in highest rated PPE regardless of what was establised when plants were isolated to account for possible higher Arc Flash vaules.
I am interested to hear what others have done in a similar situation.