... Glad this cable isn't NEC listed, otherwise....
The listing doesn't really have anything to do with this...it is just physics. A given amount of copper, no matter what type of cable it is, will carry x amount of current with x amount of temperature rise. That doesn't change when you put it in an NEC application, what changes is the NEC has limits on the permitted temperature rise.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I'm not sure how long your cables will be, but with that much current at a relatively low voltage, you should also consider the effect of voltage drop along the cables.
 