As a home inspector, I was recently helping a fellow inspector on a large house with two main panels side by side with a 150A main in each. State SOP says as inspectors we inform the buyer of the "Amperage and voltage rating of electrical service". He stated while looking at the two mains, "two 150 breakers, total 300A". I told him no, it's 200A based on the SE cable size at the meter which in this case was 200A cable. We went back and forth and agreed to disagree. What I'm looking for is any definitive answer on how to calculate Service Size when you have multiple mains and educate him, unless I'm wrong. NEC doesn't say anything about adding breaker sizes for multiple panels... just 230.2 "A building... shall be supplied by only one service..." Is there something else I'm missing? Thanks and stay safe!