wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
This is the correct answer. Given the above exception, if there is more than one service disconnect on a single service, adding the disconnect sizes does not give you the service size. Rather, you need to investigate all the equipment from the service point to the point where the service conductors divide, and use the lowest rating of those conductors/equipment.230.90(A) Exception 3 allows two 150A breakers on a 200A service so long as the load calc is 200A or less.
Cheers, Wayne