We recently had an Arc Flash study completed here at our facility and I am in the process of taking the reults from this study and implementing them in the field in order to determine what PPE levels are required for a given task on a given piece of equipment. One of the challenges I am coming across is determining what kind of tasks require Arc Flash PPE.
From NFPA 70E article 100 the FPN 1 under the definition for Arc Flash Hazard states the following:
"An arc flash hazard may exist when energized electrical conductors or circuit parts are exposed or when they are within equipment in a guarded or enclosed condition, provided a person in interacting with the equipment in such a manner that could cause an electric arc. Under normal operating conditions, enclosed energized equipment that has been properly installed and maintained is not likely to pose an arc flash hazard."
Reading this I am trying to apply it to the following conditions and wanted to hear others opinions.
4.16kV switchgear
When troubleshooting or taking measurements in the control cubilce of the switchgear is it necessary to wear required necessary Arc Flash PPE. I would think yes since you are interacting with the system.
When racking in or closing a breaker, contactor, or switch, I would think that this would be considered interacting with the equipment and therefore would require the necessary Arc Flash PPE.
When reading meters etc.. even though you may be in the Arc Flash boundary you are not interfacing with the equipment and therfore no PPE would be required.
480V MCC
When opening a bucket (bucket breaker on or off) to work inside the bucket or take measurments do you need then necessary required Arc Flash PPE? I would think that in this case since there are live circuit conductors exposed then the answer would be yes? Even if you were working inside the bucket to change a small 120V control fuse?
When racking in a 480V bucket even though you are not exposed to live circuit conductors you are still interacting with the system and therefore need to wear the required PPE.
When operating the handle of a 480V circuit breaker with the door closed do you need to wear the required Arc Flash PPE? I would think this would be a case where you are interacting with the equipment.
I'd appreciate anyones comments or guidance on my questins related to which tasks need to follow the required PPE as defined in an Arc Flash report.
From NFPA 70E article 100 the FPN 1 under the definition for Arc Flash Hazard states the following:
"An arc flash hazard may exist when energized electrical conductors or circuit parts are exposed or when they are within equipment in a guarded or enclosed condition, provided a person in interacting with the equipment in such a manner that could cause an electric arc. Under normal operating conditions, enclosed energized equipment that has been properly installed and maintained is not likely to pose an arc flash hazard."
Reading this I am trying to apply it to the following conditions and wanted to hear others opinions.
4.16kV switchgear
When troubleshooting or taking measurements in the control cubilce of the switchgear is it necessary to wear required necessary Arc Flash PPE. I would think yes since you are interacting with the system.
When racking in or closing a breaker, contactor, or switch, I would think that this would be considered interacting with the equipment and therefore would require the necessary Arc Flash PPE.
When reading meters etc.. even though you may be in the Arc Flash boundary you are not interfacing with the equipment and therfore no PPE would be required.
480V MCC
When opening a bucket (bucket breaker on or off) to work inside the bucket or take measurments do you need then necessary required Arc Flash PPE? I would think that in this case since there are live circuit conductors exposed then the answer would be yes? Even if you were working inside the bucket to change a small 120V control fuse?
When racking in a 480V bucket even though you are not exposed to live circuit conductors you are still interacting with the system and therefore need to wear the required PPE.
When operating the handle of a 480V circuit breaker with the door closed do you need to wear the required Arc Flash PPE? I would think this would be a case where you are interacting with the equipment.
I'd appreciate anyones comments or guidance on my questins related to which tasks need to follow the required PPE as defined in an Arc Flash report.