plate
- South East PA
ADS74, Typically we don't take a 3 conductor cable and use all three conductors for one phase. In each cable there is an A phase, B phase and C phase.
If I understand you, you want to use a total of (6) 3 conductor cables, where each conductor is 300mm^2. The understanding is that the ampacity of that cable (based on the rating of its insulation) is rated at 312 Amps.
This gives you a total ampacity of 312*6=1872 Amps. I suggest that you add another cable and have (7) all together. Just a thought.