A customer is asking me to install a 400KW 8' from an 20' tall, double walled, above ground diesel storage tank that supplies a roll up generator. Would this be considered a dispensing station (ART 500) and require 20' clearance?

The customer claims that their insurance company has signed off on the installation.

Thanks for the help.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
A customer is asking me to install a 400KW 8' from an 20' tall, double walled, above ground diesel storage tank that supplies a roll up generator. Would this be considered a dispensing station (ART 500) and require 20' clearance?

The customer claims that their insurance company has signed off on the installation.

Thanks for the help.
Does it dispense anything?
 