different color coductors

Status
Not open for further replies.

kjless

Member
Location
plaistow nh
at this job we are doing now we have a bunch of motors some are 208 and some are 480 does it say anywhere in the code the the conductors have to be color coded to the voltage supplying them. most of the motors are fed with mc but some of the mc cables at different voltages enter an enclosure. I'm trying to get away with using i color mc cable if so where does it say that
 
Take a look at 210.5(C) for identification of branch circuits and 215.12(C) for identification of feeder conductors. Keep in mind that the 2008 NEC expanded the requirement for identification of ungrounded conductors.

Chris
 