inspector 102
Senior Member
- Location
- Northern Indiana
Have a 3 phase meter that serve a 200 amp 3 phase disco and a 200 amp single phase disco that has all 5 conductors running through a 2 1/2 RMC into a gutter then into each disco. Is there an issue with single phase and 3 phase in the same conduit. Conduit fill does not appear to be issue ( .3117 x 5 = 1.5585, 1.946 allowable @ 40%). Is there a concern of heat build-up or parallel conductors? Thank for advice.