- Windsor, CO NEC: 2023
- Hospital Master Electrician
I have a situation where a friend asked me to take a look at a receptacle that showed up on a HI report as being reversed polarity, and I agreed. When I took the receptacle out, sure enough, it was simply wired backwards and so I went about correcting it.
I noticed there was one EGC and four circuit conductors, and I didn't see a splice on the EGC. I stooped over and looked closer, and discovered that the cable exiting the box had the EGC snipped where it entered the box.
I quickly plug-checked the other receptacles in the room, which all read fine. I then whipped out my wiggy and tested for continuity between the receptacle's faceplate screws, and they were fine.
But then I tested between the receptacle faceplate screws and a nearby switch's faceplate screws, and discovered that the switch wasn't bonded. I checked around a bit more and discovered all the switches in the basement weren't bonded.
I imagine after the house was built the then-owner finished the basement without inspection, years ago. Now, the current owner has inherited the problem.
Since the wiring is all concealed, and the whole area is finished, what would you recommend? I have no idea when the wiring was completed, but it's pretty clear from the use of NM cable with ground that EGCs were required at the time of installation.
I am concerned with the safety of the basement, but am not sure what to recommend be done about it.