Class 1 vs. Class 2 Wiring
The issue of Class 1 (line voltage) and Class 2 (low-voltage) wiring has to do with whether or not the low-voltage
0-10 V signal can be run in the same conduit as the line voltage wiring. This is often a question that deals with
local codes and the capabilities of the ballast / driver and control. Local codes that allow Class 2 wiring to be
run as Class 1 will call out requirements for re-classification. These requirements often include adding “Class 1”
labels over the “Class 2” markings on devices, larger wire gauges, and different insulation requirements. Some
jurisdictions do not allow for re-classification.
Running the 0-10 V signal as Class 1 wiring does introduce some other concerns, including noise / interference
caused by coupling between the line voltage and low-voltage wires. This noise / interference can cause a voltage
fluctuation on the 0-10 V wires which can create a difference between the light level requested by the control and
the light level signal being received by the ballast / driver.
When using Lutron EcoSystem devices, the EcoSystem loop is capable of being run as Class 1 or Class 2
wiring (if allowable by local codes) by following the proper re-classification steps. The digital nature of the
communication eliminates the noise / interference concern because the communication does not rely on
measuring small changes in the voltage.