Here is one I have not seen before. Kind of exciting really...here goes. A client is complaining about dimming lights when other loads come on. When I turn on the microwave...the lights dim and the MW seems to bog. Testing the outlet shows 112V with MW off and 104V with it on. The dimming seems to be housewide. I go to the panel and have, coming into the main bkr, 112V on one leg and 126V on the other...with MW on I have 104V and 130V. Pop the meter and all connections are tight. With main bkr off...I have 120/120 ( problem not from the street ). Turn main back ( with all others off ) and get 120/120. Turn on bkrs one at a time and identify 2 single pole bkrs ( on different phases ) and a 2 pole 50 that all seem to tweak the voltage to 112/126. The 2 pole 50 is too an older fuse box ( still fused ). I had to leave before I could get any further. Any ideas? Neutral maybe....but it seems to be on at least 3 independent cables.....and then why would it affect the whole house? Incoming neutral? then why only the few brks? Any words of wisdom appreciated in advance.