Dimming lighting???

Status
Not open for further replies.
Too much load already on the circuit when you turn it on.

Sometimes, plugging into a different circuit will 'cure' it. Otherwise, either learn to live with it, run a dedicated circuit or vacuum without the lights off.
 
Too much load already on the circuit when you turn it on.

Sometimes, plugging into a different circuit will 'cure' it. Otherwise, either learn to live with it, run a dedicated circuit or vacuum without the lights off.

Learn to live with it would be my suggestion, a dedicated circuit will not necessary fix the dimming complaint.
 
081224-1440 EST

The amount of change in voltage on the load side of a voltage source with some internal impedance from an addition of a load is relatively independent of the pre-existing load on the circuit if the said source impedance is small compared to the load. This is the general design of a power system.

In a typical application there is a source, pole transformer, with its source impedance. Also wires from the transformer to the main panel with their addition to the source impedance as seen at the main panel. Then there are many branch circuits running from the main panel.

Suppose the source impedance at the main panel and looking toward the transformer is 0.005 ohms. Then the drop in voltage as seen at the main panel is 0.05 V for a 10 A load. Startup current on a small motor might be 70 A and this would cause a drop in voltage of 0.35 V.

Next go to the end of a 50 ft run of #12 wire. This has a loop resistance of .16 ohms. 70 A thru this is a voltage drop of 11.2 V. If your lamp is at the end of the branch where the motor is also located, then you will see a substantial flicker. If you put the lamp on a different circuit, then it only experiences a change of 0.35 V and this is a much reduced flicker.

Note: Your voltage drop at the motor is actually 0.35 + 11.2.

.
 
What if you did a service upgrade and it still dimmed????? And then you found out it had a loose connection on the power company's transformer nuetral???????????????
 
What if you did a service upgrade and it still dimmed????? And then you found out it had a loose connection on the power company's transformer nuetral???????????????

More than likely, I would have found that well before I suggest a new circuit. I don't hunt squirrels with an elephant gun.
 
Last edited:
now I'm really confused. Doesn't take much.:smile:
he had said for you too vacuum without the lights off. Well in order for you to vacuum without the lights off you would have to turn them on. Which is what is usually the case anyway. The lights are usually on already. I was just picking on him. What he should of said was vacuum with the lights off.
 