Dimming Wires

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
We use 18 AWG Stranded TFFN, pulled in with power conductors in conduit:
https://www.encorewire.com/wp-content/uploads/EncoreWire-TFFN.pdf
Its rated 600V, and listed under 725.49(B)

I would prefer a label 'Class 1 system' rather than the sharpie blackout.

I would encourage you to pick obvious colors that are not used in your building.
There was a tenancy to use grey and purple which I have seen mistakenly connected to neutrals.
I spec yellow and purple.
Cheers
Yellow is commonly used as one of the 277/480 colors, just like the grey often is for the 277 neutral.
 

jusme123

Senior Member
Location
NY
Occupation
JW
So what's crazy to me is if you have a job that's full conduit you have to run two separate conduits to each fixture one for dimming wires and one for power. On a big job that can be a huge cost. Thanks

Sent from my SM-N960U using Tapatalk
Buy the MC (MC Luminary) with control wires within power cable, you’ll thank me later, huge time/ headache saver
 
Last edited: